Study of Numerical Overcurrent Relay
#1

Study of Numerical Overcurrent Relay


.docx   Indika_NumericalRelay.docx (Size: 74.26 KB / Downloads: 133)

DISCUSSION
• Three stage over current Characteristics of the KCGG relay

Three stages of KCGG relay is shown above and this relay is used for time graded over current and earth fault protection. These stages have threshold limits and time delays which are independent from each other
Furthermore, for phase faults and earth faults separate settings have defined (for phase faults - I>, earth faults - Io>). Relay operates when the power frequency component of the current exceeds the set threshold. These elements may be set as a low set overload protection and may be expected to have relatively long associated time delays. In the first stage several inverse time curves and definite time characteristics are available. In addition adjustable reset timer also provided for intermittent faults. Stage 2 and 3 facilitates for instantaneous tripping using definite time setting. Therefore according to user requirement, suitable characteristic can be obtained setting those parameters appropriately in three stages.



Advantages of having various Time/Current characteristics.
In power systems there are many power protection methods and elements. These relays are used not only as main protection elements, but also backup protections such as after fuses. So relays must coordinate with the thermal characteristics of fuses and coordinate and grade with other protection schemes and devices easily. Usually numerical relays are having various time/current characteristics because of the above reasons. Relay is provided with seven inverse time/current characteristics to cover the range of applications to which the relay may be applied.



Discuss the operation of IDMT Relay coordination system
In earlier most of the overcurrent relay works on the induction principle. The moving system consists of an aluminum disc fixed on a vertical shaft and rotating on two jeweled bearings between the poles of an electromagnet and a damping magnet. The winding of the electromagnet is provided with seven taps generally, which are brought on the front panel and the required tap is selected by a push-in -type plug. The pick-upcurrent setting can thus be varied by the use of such plug multiplier setting. Thepick-up current values of earth fault relays are normally quite low.The operating time of all overcurrent relays tends to become asymptotic to a definiteminimum value with increase in the value of current. This is an inherent property ofthe electromagnetic relays due to saturation of the magnetic circuit. By varying thepoint of saturation, different characteristics can be obtained and these are

1. Definite time
2. Inverse Definite Minimum Time (IDMT)
3. Very Inverse
4. Extremely Inverse






Reply

Marked Categories : over current relay, relay, overcurrent relay, case study on numerical relay, numerical over current relay, numerical overcurrent and earth fault relay full report, over current kcgg relay, numerical overcurrent relay ppt, time current charactristics of over current relay ppt, seminar on numeric relays, kcgg relay characteristic curve, three stage overcurrent characteristic of kcgg relay, numerical relay seminar topic, overcurrent relay project report, three stage of over current relay, project report on overcurrent relay, operation of idmt relay coordination system, 3 stages of kcgg relay, idmt relay, three stage over current characteristics of the kcgg relay,

[-]
Quick Reply
Message
Type your reply to this message here.

Image Verification
Please enter the text contained within the image into the text box below it. This process is used to prevent automated spam bots.
Image Verification
(case insensitive)

Possibly Related Threads...
Thread Author Replies Views Last Post
  Directional Overcurrent Relaying (67) Concepts project girl 1 2,011 19-09-2017, 04:37 PM
Last Post: jaseela123
  STUDY OF BASIC DIGITAL IC’s study tips 1 1,040 13-09-2017, 01:18 PM
Last Post: jaseela123
  STATIC OVERCURRENT RELAY REPORT project girl 1 3,065 13-09-2017, 10:33 AM
Last Post: jaseela123
  Relay Driver Circuit Report seminar projects maker 1 800 07-09-2017, 10:21 AM
Last Post: jaseela123
  To study the construction and working of single phase energy meter dhanabhagya 0 464 12-02-2016, 04:52 PM
Last Post: dhanabhagya
  Comparative study of different dielectrics for micro-EDM performance dhanabhagya 0 425 10-02-2016, 04:56 PM
Last Post: dhanabhagya
  STUDY OF GATE FIRING CIRCUITS project girl 1 4,574 14-12-2015, 06:28 PM
Last Post: Guest
  STUDY OF 400KV SWITCHYARD & PROTECTION project maker 0 829 01-08-2014, 12:45 PM
Last Post: project maker
  Numerical Relaying Fundamentals project maker 0 497 27-06-2014, 03:09 PM
Last Post: project maker
  Study on protection Scheme for Micro-grid with Mobile Energy Storage Units pdf seminar post 0 468 19-05-2014, 04:57 PM
Last Post: seminar post
This Page May Contain What is Study of Numerical Overcurrent Relay And Latest Information/News About Study of Numerical Overcurrent Relay,If Not ...Use Search to get more info about Study of Numerical Overcurrent Relay Or Ask Here

Options: